你现在位置:首页>技术论文>电气常识>理论学习>正文
PID Instruction
日期:2008-3-22 12:26:54 来源:本站整理
1. Integer PID Instruction
This instruction is for 12 bits analog, i.e. raw value range should be from 0 to 4095 (0% to 100%) only.
1.1 Instruction Syntax
[PID %MWx]
%MWX is from %mw0 to %mw487, 24 continue registers are required for this instruction.
1.2 Instruction Representation:
1.2.1
%MWx
Loop Status Register
See table below
Loop status register
Bit
Meaning
15
Node Lockout or Parameter Error
14
High Alarm
Low Alarm
Time since last solution >= solution interval
10
Loop is not being solved
Sign = E stored in Mwx22 , 0=+, 1= -.
Integral windup limit never set
Integral windup saturated
Negative values in the equation
3
Manual/Auto Input
%MWx+1
Error Status bits
See table below
Code
Explanation
Register should be checked
No errors, all validations OK
None
SP above4095
%MWx+2
High alarm above 4095
%MWx+4
0003
Low alarm above 4095
%MWx+5
0004
Proportional band below 5
%MWx+6
0005
Proportional band above 500
%MWx+6
Reset above 99.99 r/min
%MWx+7
Rate above 99.99 min
%MWx+8
0008
Bias above 4095
%MWx+9
0009
High integral limit above 4095
%MWx+10
Low integral limit above 4095
%MWx+11
High output clamp above 4095
%MWx+13
Low output clamp above 4095
%MWx+14
Low output clamp above high output clamp
%MWx+13 and %MWx+14
GL below 2
%MWx+15
GL above 30
%MWx+15
Insufficient %Mw register remained
%Mwx
1.2.3
%MWx+2
SP
You must specify the set point in raw data units; the value must be in range of 0~ 4095.
%MWx+3
Mv
Loaded by the block every time the loop is solved; it is clamped to a range of 0 ... 4095, making the output compatible with an analog output module; the manipulated variable register may be used for further CPU calculations such as cascaded loops
%MWx+4
High Alarm Limit
Load a value in this register to specify a high alarm for PV (at or above SP); enter the value in range of 0~ 4095.
%MWx+5
Low Alarm Limit
Load a value in this register to specify a low alarm for PV (at or below SP); enter the value in range of 0~ 4095.
%MWx+6
Proportional Band
Load this register with the desired proportional constant in the range 5 ... 500; the smaller the number, the larger the proportional contribution; a valid number is required in this register for PID instruction to operate
%MWx+7
Reset Time Constant
Load this register to add integral action to the calculation; enter a value between 0000 ... 9999 to represent a range of 00.00 ... 99.99 repeats/min; the larger the number, the larger the integral contribution; a value > 9999 stops the PID instruction calculation
%MWx+8
Rate Time Constant
Load this register to add derivative action to the calculation; enter a value between 0000 ... 9999 to represent a range of 00.00 ... 99.99 min; the larger the number, the larger the derivative contribution; a value > 9999 stops the PID instruction calculation
%MWx+9
Bias
Load this register to add a bias to the output; the value must be between 000 .... 4095, and added directly to Mv, whether the integral term is enabled or not
%MWx+10
High Integral Windup Limit
Load this register with the upper limit of the output value (between 0 ... 4095) where the anti-reset windup takes effect; the updating of the integral sum is stopped if it goes above this value—this is normally 4095
%MWx+11
Low Integral Windup Limit
Load this register with the lower limit of the output value (between 0 ... 4095) where the anti-reset windup takes effect—this is normally 0
%MWx+12
Raw Analog Measurement
The logic program loads this register with PV; the measurement must be scaled and linear in the range 0 ... 4095
%MWx+13
Output Clamp— High
The value entered in this register determines the upper limit of Mv—this is normally 4095
%MWx+14
Output Clamp— Low
The value entered in this register determines the lower limit of Mv—this is normally 0
%MWx+15
Rate Gain Limit (RGL) Constant
the value entered in this register determines the effective degree of derivative filtering; the range is from 2 ... 30; the smaller the value, the more filtering takes place
%MWx+16
solution interval
solution interval, 1 to 255 represent 0.1 to 25.5 second
Note: Only %MWx+2 to %Mwx+15, and bit 1 of %MWx  are filled out by user.
上一篇: CV值计算
下一篇: 仪表工习题